Plumbing / Central Heating Help Please.


Page 1 of 2 1 2 > Last >>
martin2412 Flag Living The Dream 29 Mar 16 10.43am

I currently can only get hot water if I have the heating on. I'm told that the motorised valve needs replacing (or just the head) which looks simple enough to do myself.

If i switch my boiler on to 'water only' it doesn't fire up. Does anyone know if I replace the motorised valve that this will correct this.

Thanks in advance.

 

Hoof Hearted 29 Mar 16 10.52am

[Link]

This video might help?

 

Kermit8 Flag Hevon 29 Mar 16 10.55am

There's a rather helpful plumber on the BBS site if you sign up.

 


Big chest and massive boobs

[Link]


Apollofuzz Flag On the edge of reason 29 Mar 16 11.09am

It could well be the motorised valve. You will need to replace the solenoid on the valve easy job to do dependent on the type of valve. New Solenoid is about £15.

 


I ride a GS scooter with my hair cut neat
I wear my war time coat in the wind and sleet.

martin2412 Flag Living The Dream 29 Mar 16 11.28am

Originally posted by Apollofuzz

It could well be the motorised valve. You will need to replace the solenoid on the valve easy job to do dependent on the type of valve. New Solenoid is about £15.

Thanks. Do you know whether a faulty motorised valve would stop the boiler from firing-up on 'water only' ?

Cheers all who have answered.

 

martin2412 Flag Living The Dream 29 Mar 16 11.32am

Originally posted by Kermit8

There's a rather helpful plumber on the BBS site if you sign up.

Cheers Kerms. I've been signed up to the BBS for years but have never posted - I would feel dirty.

 

Pikester Flag Worthing 29 Mar 16 12.48pm

Hold the front page! I may be about to be helpful.

I had a similar problem where my central heating wouldn't turn off.

I needed to replace the top bit of the valve: [Link]

You should have 2 of these in your airing cupboard (providing you don't have a combi boiler) - one controls the heating the other the hot water.
On the back of each is a small piece of metal that you can manually slide over and it should slowly spring back into position. If one of them is jammed or really loose that'll be the problem.

You can replace the top part only without needing to do any plumbing (although it does have about 7 wires that you'll need to connect)
If you need to replace the whole unit that's a trickier problem.

My nephew on here (Eddie_Hitler) may log on for the first time in 10 years and be of help - he talked me through analyzing my issue and I managed to replace it myself.

PS: Turn the power off before you attempt to replace it. But if you don't can I have your semi-final ticket?

 


You fed me, you bred me, I'll remember your name.

martin2412 Flag Living The Dream 29 Mar 16 1.01pm

Originally posted by Pikester

Hold the front page! I may be about to be helpful.

I had a similar problem where my central heating wouldn't turn off.

I needed to replace the top bit of the valve: [Link]

You should have 2 of these in your airing cupboard (providing you don't have a combi boiler) - one controls the heating the other the hot water.
On the back of each is a small piece of metal that you can manually slide over and it should slowly spring back into position. If one of them is jammed or really loose that'll be the problem.

You can replace the top part only without needing to do any plumbing (although it does have about 7 wires that you'll need to connect)
If you need to replace the whole unit that's a trickier problem.

My nephew on here (Eddie_Hitler) may log on for the first time in 10 years and be of help - he talked me through analyzing my issue and I managed to replace it myself.

PS: Turn the power off before you attempt to replace it. But if you don't can I have your semi-final ticket?

Cheers Pikester, and yes if I get frazzled, the ticket's yours !

 

Ted the eagle Flag Waddon 29 Mar 16 1.04pm

Originally posted by martin2412

I currently can only get hot water if I have the heating on. I'm told that the motorised valve needs replacing (or just the head) which looks simple enough to do myself.

If i switch my boiler on to 'water only' it doesn't fire up. Does anyone know if I replace the motorised valve that this will correct this.

Thanks in advance.

Probably the diverter valve - try turning the power to the boiler off, then back on (listen closely). This resets the valve position, or at least it does on my Worcester (may have to do a couple of times). Had it happen a couple of times before where the heating wasn't used in the summer... . the valve gets jammed.

Hope this helps.

 

Jimenez Flag SELHURSTPARKCHESTER,DA BRONX 29 Mar 16 2.01pm

Originally posted by Ted the eagle

Probably the diverter valve - try turning the power to the boiler off, then back on (listen closely). This resets the valve position, or at least it does on my Worcester (may have to do a couple of times). Had it happen a couple of times before where the heating wasn't used in the summer... . the valve gets jammed.

Hope this helps.

In other words Ted a rework of the old but trusted 'Turn it off & turn it back on' Trick

Edited by Jimenez (29 Mar 2016 2.02pm)

 


Pro USA & Israel

JL85 Flag London,SE9 29 Mar 16 2.11pm

You'll either have 2 x 2 port valves (one for heating and one for hot water) or 1x 3 port Valve that does both.

If the hot water only works with the heating then it may suggest the motor on the valve isn't modulating. These can be modulated by hand. Give it a try.

 

martin2412 Flag Living The Dream 29 Mar 16 3.19pm

Originally posted by JL85

You'll either have 2 x 2 port valves (one for heating and one for hot water) or 1x 3 port Valve that does both.

If the hot water only works with the heating then it may suggest the motor on the valve isn't modulating. These can be modulated by hand. Give it a try.

Cheers JL

I didn't even realise I had two different valves (well I have only lived here for 8 years)!

There is one valve downstairs beside the actual boiler (in a cupboard which looks like a git to get at). The lever on this one has some resistance when you try to move it across. There is also one upstairs next to the hot water tank which has no resistance at all, and I'm assuming that it is this one which may be cream crackered. I'll replace this one first, but you know what's going to happen don't you.

Appreciate your help.

 

kingdowieonthewall Flag Sussex, ex-Cronx. 29 Mar 16 3.56pm

Martin, As you know, I am a painter & as such know f*** all about plumbing & even less about central heating.
However, you needn't bother with any of the above advice.
Just turn the immersion heater On & off whenever you want hot water or better still leave it on constantly.
Bingo. Hot water forever
(and an electricity bill so big that you'll have to sell a kidney to cover)

 


Kids,tired of being bothered by your pesky parents?
Then leave home, get a job & pay your own bills, while you still know everything.

Alboss Flag South North Wood 29 Mar 16 4.05pm

If the lever is lose that means that the motor has moved to the 'on' position. However if it is not turning the pump and boiler on it sounds like the valve isn't hitting the microswitch... Turn off the mains power before attempting anything. Take off the top of the valve and you will see the motor which is held in by one (tiny) screw. Undo that and cut the two wires attaching it to the valve. The new motor will have two wire connectors so you can then twist the wiring back together. Put the motor in position, screw it in place and that's that. I'd that doesn't work, it could be the whole valve head.

Without sounding too precious... Please be careful

 

Hoof Hearted 29 Mar 16 4.08pm

Originally posted by Pikester

Hold the front page! I may be about to be helpful.

I had a similar problem where my central heating wouldn't turn off.

I needed to replace the top bit of the valve: [Link]

You should have 2 of these in your airing cupboard (providing you don't have a combi boiler) - one controls the heating the other the hot water.
On the back of each is a small piece of metal that you can manually slide over and it should slowly spring back into position. If one of them is jammed or really loose that'll be the problem.

You can replace the top part only without needing to do any plumbing (although it does have about 7 wires that you'll need to connect)
If you need to replace the whole unit that's a trickier problem.

My nephew on here (Eddie_Hitler) may log on for the first time in 10 years and be of help - he talked me through analyzing my issue and I managed to replace it myself.

PS: Turn the power off before you attempt to replace it. But if you don't can I have your semi-final ticket?

Be honest Pikey - did you just watch the video I posted up earlier in the thread?

The bloke on that video said pretty much what you've just said.

.... or... are you that bloke on the video... Baldy!

 

Pikester Flag Worthing 29 Mar 16 4.20pm

Originally posted by Hoof Hearted

Be honest Pikey - did you just watch the video I posted up earlier in the thread?

The bloke on that video said pretty much what you've just said.

.... or... are you that bloke on the video... Baldy!

I'm unable to watch videos on the internet software we have in the office - so if that bloke is saying the same as me then there's 2 possible scenarios:
a)I'm a bit of a genius
b)He's as much of a f***wit as I am!

And I still have all of my own hair thanks!*

* - in a box under the bed.

 


You fed me, you bred me, I'll remember your name.

Hoof Hearted 29 Mar 16 4.38pm

Originally posted by Pikester

I'm unable to watch videos on the internet software we have in the office - so if that bloke is saying the same as me then there's 2 possible scenarios:
a)I'm a bit of a genius
b)He's as much of a f***wit as I am!

And I still have all of my own hair thanks!*

* - in a box under the bed.

I'll opt for ( a ) then.

Seriously.... the OP has thanked everyone on here personally but me and I gave him the right answer in an easy to follow video pretty much minutes after he asked for help.

Edited by Hoof Hearted (29 Mar 2016 4.39pm)

 

Kermit8 Flag Hevon 29 Mar 16 4.42pm

Originally posted by Hoof Hearted

I'll opt for ( a ) then.

Seriously.... the OP has thanked everyone on here personally but me and I gave him the right answer in an easy to follow video pretty much minutes after he asked for help.

Edited by Hoof Hearted (29 Mar 2016 4.39pm)


You should be content in the knowledge that you gave and had no need to receive if you'll pardon the gay inference when all we are talking about is ballcocks and suchlike.

 


Big chest and massive boobs

[Link]


kayjaybee Flag orpington 29 Mar 16 4.47pm

Originally posted by Hoof Hearted

I'll opt for ( a ) then.

Seriously.... the OP has thanked everyone on here personally but me and I gave him the right answer in an easy to follow video pretty much minutes after he asked for help.

Edited by Hoof Hearted (29 Mar 2016 4.39pm)

sometimes don't it make you wonder why you bother, eh hoof,

 

Apollofuzz Flag On the edge of reason 29 Mar 16 5.11pm

Originally posted by martin2412

Thanks. Do you know whether a faulty motorised valve would stop the boiler from firing-up on 'water only' ?

Cheers all who have answered.

Sorry for not replying sooner. The answer is yes as the synchro (the little motor bit on top) does turn the valve which tells the boiler to start. As others have said you can manually move the valve with the little Lever on the side. This should force the boiler to fire. Make sure you turn the power off before disconnecting the motor. The new one will have two wires which you will need to connect to the old ones the wires are very thin. use a small terminal block or wire connectors. To find out which is which turn just the heating on and see which pipe gets hot as a guess the one near your cylinder is your hot water but it could be either. Good luck


Edited by Apollofuzz (29 Mar 2016 8.56pm)

 


I ride a GS scooter with my hair cut neat
I wear my war time coat in the wind and sleet.